RandyB
Retired
- Nov 15, 2019
- Portage, MI
- Ventana LE 4037
- 40' 11"
- 2021 Chevy Trailblazer
2017 Ventana LE 4037
Onan 8HDKAK-1046N
MS2012 Inverter
Precision Circuits Inc Central Monitor Panel
No shore power. Generator running, and waiting for the 30 second delay before starting anything. I could here the "thump" of the relay pull in at 30 seconds, but it was not quite as loud as what I remember compared to the shore power relay.
Line 1 = Zone 1 AC on and cooling
Line 2 = Zone 2 AC on and cooling
Voltage reading on the Central monitor panel:
What's so weird is the 0 volts with 14 amps and the AC on that line is running just fine.
Then, looking at another page of the Control panel is the error code:
At the transfer switch relay, the voltages are as follows:
Red to White = 120 volts
Black to White = 120 volts
Black to Red = 0 volts
Green to White = 0 volts, with continuity
Isn't the voltage between the 2 leads red and black supposed to equal 240 volts?
What does the error code mean in the display?
Here is another page of the display:
By the way, I have looked at the "manual" from PCI. The copy I have is quite worthless. There have been no changes made since the last operation of the systems when everything was fine.
To summarize my questions:
1. How can the display read 0 volts with 14 amps and the devices being run are just fine?
2. Are the volts between red and black supposed to be 240 on generator?
3. What does the control panel display error code mean or indicate?
Note: I am not using the coach at this moment, it is in storage facility, so access is not immediate, but possible with time.
Onan 8HDKAK-1046N
MS2012 Inverter