Great question and i wish i had a good answer. The process started because i had some electrical issues using the inverter. The mechanic from Michigan indicated that he has not worked with inverter power in the past. However, he was recommended buy a repair facility that had always done a great job for me, so i went with him. He didn't tell me of the 30 amp only until he was done and i came to pick it up. We live invthe rv during the summer months and we needed to get back in our home so i though we could work around it but it's been very inconvenient, especially for my wife. I hope this background explanation provides some insight.Welcome to RVF, @Louisfarm; glad to have you here. It sounds like your previous 50A inverter failed and was replaced with a 30A unit. Is that correct?
Restoring 50A capability will likely require replacing the 30A unit with one rated for 50A. Was there some reason why the 30A unit was installed? Usually, a replacement unit is rated for the same capacity as the one it replaces.
TJ
My Safari Simba was working with 50 amp service and inverting 50 amps using a renogy 3000 watt inverter or shore connection of 50 amp. Mechanic put in a 30 amp inverter (ms2012 Magna) and resticted the shore power to 30 amps. What do i need to get it back to 50 amp?
First of all, thanks for the thorough and clear explanation. The way it was wired to the main bus is the shore & generator power coming from the transfer switch goes into a 50 amp double pole breaker and has a 30 amp breaker (not shown in picture) feeding back to the 30 amp inverter on #10 wire, (2) 20 amp breakers for front and back A/C, hot water heater and vacuum in basement. At this point I'm wondering how the refrigerator, microwave and plugs throughout the unit are being supplied with power (no breakers feeding them from main bus)?We really need to know your wiring architecture. For example...my coach is 50A and uses a 30A input to the inverter (MS2812)
Shore power cord (50A) >>>>>> 50A surge protector >>>> transfer switch.
Generator >>>>>>>>transfer switch.
Transfer switch takes one (generator priority) >>>>>>>>Precision Circuits Load Center.
Precision Circuits load center is divided into two buses...a MAIN...and an Inverter.
The main bus gets it’s input from the transfer switch and is protected by a pair of 50A breakers. The main bus has branch breakers for air conditioners, washer, dryer, water heater element, block heater, and a 30A branch supplying the MS2812 Inverter.
Output from the inverter comes back to the panel and feeds the Inverter bus thru a 30A breaker. The smaller Inverter bus has branch circuits for kitchen outlets, residential fridge, microwave, entertainment system outlets, etc...
Using the Inverter you have now...the above architecture should work. The power cord, and transfer switch wiring will have to be upgraded to #6 (50A ampacity) vs #10 (30A ampacity).