I would fully charge the batteries...then disconnect the batteries...let them sit for at least 2 hrs to dissipate any surface charge...take voltage readings for each battery...and specific gravity reading for each cell. This will help identify a weakened battery or cell. Crowne is a reputable mfg...I feel somewhat confident that plate erosion is NOT your concern. Sulphation is the enemy. When you discharge the battery the sulfuric acid reacts with lead to form depisits of Lead Sulphate on the plates. Recharging should dissolve this deposited and put the irons back into the liquid solution. Your specific gravity measures this. A fully charged battery should have a particular specific gravity...if you notice your batteries do not meet this benchmark...of note, you are victim to suplhation that has not dissolved back into solution. This robs your battery of capacity. Ideally, we all would be measuring our specific gravity each quarter...and if a battery is low, or I individual cells show variance...we do the equalization or conditioning charge. There are some commercial tonics which are claimed to help with this...and Battery Minder uses high frequency pulses to help desulohate a battery. May be worth a try on such young batteries.
The way you have them wired...although I am guilty of the same...is not ideal. Ideally, the pathways should be equal. Your leads take a shorter path across the front two...and a longer path across the rear two. This will make one pair work more than the other. In future cabling design...especially since your shunt goes to one location...best practice is most positive and most negative. The pathway across any pair should be equal length...length of cables or jumper bars... This way the resistance is the same. It goes along with the idea that batteries should all be changed as a set...of equal capacity and age.
I kinda wave the BS flag on amperage. Amperage is a rate. I may be wrong, but equalization/desulphating is done off of voltage... I think it is quite possible that you didn't do this often enough...again, we all are probably guilty of this. The longer sulphate are left on the plates...the more difficult they are to redissolve.
The enemy is allowing a battery to sit in a discharged state. If you had your batteries on a charger, they should have stayed fully charged. I rarely see amperage get much above 10A each day when my solar system wakes and brings my bank up to absorption voltage, then drops down to just a couple of amps to float the remainder of the day. Can high amps be good? I guess heating the solution may make a difference...but charge is charge...if the battery reaches full charge, you've done what you can to redissolve the lead sulphate.
I will probably do a few equalization rounds on my own batteries...and see if the voltage follows the common drop proportional to aH used... But don't really expect a miracle. They are 4 years old...and I expect for the capacity to go down with age. I'll hopefully notice a change in S.G. after each round...but we'll see.
Without being able to take a drop of battery acid out for testing, I'm not sure what AGM owner's use to quantify a time to equalize...