Welcome to RVForums.com

  • Register now and join the discussion
  • Friendliest RV Community on the web
  • Modern site for PC's, Phones, Tablets - no 3rd party apps required
  • Ask questions, help others, review campgrounds
  • Get the most out of the RV Lifestyle
  • Invite everyone to RVForums.com and let's have fun
  • Commercial/Vendors welcome

No AC communications

Welcome to RVForums.com

  • Register now and join the discussion
  • Modern secure site, no 3rd party apps required
  • Invite your friends and let's have fun
  • Commercial/Vendors welcome
  • Friendliest RV community on the web

gerrypratt

RVF Regular
Joined
Mar 26, 2022
Messages
11
Location
Norton, MA 02766
RV Year
2012
RV Make
Newmar
RV Model
Bay Star 3002
RV Length
30
Chassis
Ford
Engine
6.8
Fulltimer
No
No communications with Dometic CCC2 thermostat, AC, and Furnace.

Replaced zone 1 AC that was running poorly and saved control board.
Both Dometic zone 2 and new Advent AC zone 1 were working fine but furnace not recognized by Dometic CCC2 themostat.
Lost power to CCC2 thermostat.
Checked communication cables for bad connections.
Cleaned RJ11 inputs female jacks on control board.
Replaced RJ11 male jacks on all cables and checked for continuity.
All cables are twisted so black wire is on the left side of jack like dometic manual figure 5.
RJ11 cable from control box is twisted at thermostat end.
Should the daisy chain cable zone 1 to zone 2 be twisted or not?
Have 12VDC input at control board P6 pin 5 and 6
Control board shows 4.95VDC from RJ11 output fully connected at AC. Not sure what voltage it should be. I believe 12VDC.
Dometic states CCC2 can not be tested. Replace only if suspected faulty. So replaced with new CCC2 thermostat. Still no power at thermostat.
Have reset power supply several times but thermostat does not power up. AC has 12VDC and 110AC
Called Newmar dealer and they would not work on RV
Tried several other places and no wants to touch it.
Both AC's were working at one point but no furnace. Right now I would be happy with the two AC’s working.
Zone 1 dip switches are set open except for furnace dip switch which is set on.
I tried taking Zone 2 out of the loop with no success.
I switched out the new Advent AC135 control board with original working control board on old AC. Both control boards are CCC2 supported. Still no power at thermostat.
Is the RJ11 output of 4.95VDC to low? Should I buy a new control board? Have I got a cable connected wrong? I'm all screwed up at this point. Need someone who could lead me through this. Willing to pay someone if they can figure out to help me. Please help if you have dealt with this problem. Thank you.
 