Currently, I'm in a situation where my Control Panel displays different voltage readings on L1 and L2, than what is showing on the pedestal. How do you determine if it is indeed your control panel? I'm having a situation where the readings at the pedestal are different from my control panel, thus causing my AGS to turn on, but randomly despite the readings on my Control Panel. I trusted the electrician and didn't check the pedestal myself which I will do if I have another problem. Is there a way to "test" the Control Panel for effectiveness?
Renee,
It appears my perception of my PCS panel is incorrect. It is not flakey. It is measuring the potential from the Leg to Ground, instead of Leg to Neutral. The panel looks at all these things. That’s how it decides L1<>L2, or L1=L2, Neutral=Ground, L1>Neutral, L1>Ground...and tells you OK.
When I look at my Surge Protector’s display...I see normal voltage. When I plug in one of those Huges Voltage readers...normal. When I check my pole with a voltmeter...normal. Heck my distribution panel...normal. The whole time, I was referencing L1 or L2 to Neutral.
Here’s the rub. If I check Ground against Neutral...I am getting around 9v. This should be zero, or less than .5v at any rate. Now...check my L1 or L2 against Ground... Bingo...screwy display, and very close to what my PCS panel displays.
I know there is a bad Neutral or Ground connection somewhere. I think it’s the campground. I started the generator...and saw 117, 117 on the PCS panel...so my coach isn’t creating this issue when I disconnect. To me...the problem has to be transfer switch outward. Most reasonable explanation...bad shore wiring.
If I get home, plug into my pedastle and still have a potential crossing Neutral and Gound...then I must have a problem. But I am pretty certain that isn’t going to be the case.
I am looking to find something that explains how these things happen. Well, I can kinda understand that. It’s the way it causes one legs voltage to go up and the other to go down that I find unique. Hmmm.., I’m pretty cut and dry simple when it come to electricity. I understand how it works when it’s working correctly...but something a Master electrician would have caught in a second...eluded me. I went for the easy explanation —- PCS panel must be the reason. Wrong.
Before giving up on your PCS panel...I would see if you are getting the same weird voltage at the pole when you measure the Line to Ground...instead of just Line to Neutral as we normally do.