Well let me recap everything with all the information as I have it, in it’s corrected form and maybe that will put some of the questions at ease.
We were out for the day and when we came back, we came back to a perfectly functioning coach, not dead batteries as my original post indicates.
We walked in and DW got to making dinner while I got to salivating and panting. Now, we’d been hookup up to 30amp service for a week and a half without issue and I will freely admit, I’m kind of an “if it ain’t broke, don’t fix it” kinda guy. I say that because I plugged in, checked that there was power coming in and kicked back on my laurels, as I usually do. I’m not the guy watching all the systems like a hawk, but one thing I’ve learned from this experience is that I should watch them at least a little closer. A daily check of all systems in the cabinet wouldn’t interrupt the flow of my day.
So we came back to a coach. Wife was making some roasted veggies in the convection oven and some chicken wings in the Instant Pot Duo Air Fryer.
Kids are prepping the table and I’m getting ready to go take the bikes off the bike rack when everything shuts off. Now, the house lights didn’t miss a beat when this happened, so so I didn’t notice it right when it happened. DW told me we lost power but didn’t mention to me that she had just plugged in the Air Fryer and put it to work and the Convection Oven has been turned on just a few minutes before that.
So when she tells me I come inside to investigate and look at the Magnum Panel. The fault says “Dead Batt Charge” or something to that effect, there’s a pic of the panel earlier in the thread. The fault light is on and the charge light is flashing.
Being a rookie at this, I read the fault and think to myself, now how the heck did the batteries get discharged?! We’ve been hooked up the whole week! Did the power stop coming at the pedestal a couple of days ago? Why didn’t my Hughes Power Watchdog send me an alert if I wasn’t getting power?
So I go outside and check the Power Watchdog. It’s lit up white so I know its getting power from the pedestal and it’s not throwing any error codes on the device or at my phone.
Ha! It’s the inverter! I read about this on RVForums.com and that other place too so many times. Just gotta flip the breaker. Oh, the inverter breaker isn’t tripped. Well lets just reset it for good measure. Still no change. Alright, let’s go look at the inverter. Hmm. No lights. I remember this thing having lights on when it was humming. It’s definitely the inverter because the lights aren’t on. Let’s go look at the manual...
Blah blah blah, Yadav Yada - ah, there it is.
Dead Batt Charge
Remedy: Check the DC voltage on the inverter’s DC terminals and ensure it is the same as the battery bank. These two voltages should be very close (<0.5 VDC difference). If not, check to ensure all connections are tight and the fuse/circuit breaker between the inverter and battery bank is good.
This fault automatically clears if the AC power is removed or when the voltage is greater than 12.6 volts.”
Now for some reason, only the last sentence meant anything to me. Everything else might as well not have been there because I (stupidly) completely ignored it all. All I took in was “The fault automatically clears if the AC power is removed or when the voltage is greater than 12.6 volts”
Got it. Magnum panel says I’m at .5 volts. No idea how these batteries got so discharged but if I just get them back up to 12.6 volts, the fault will clear! Let’s turn on the generator. So I flip on the generator and watch the panel, nothing is changing. Maybe it takes some time I think to myself. I let it run for a solid 15-20 minutes and the voltage reading on the panel doesn’t move an inch. Okay, power is not making it to the batteries from the generator or shore power.
@FLSteve and
@VTPete mention the generator breaker and the 300amp fuse.
I check the generator breaker and its set to on. I do a continuity test on the 300amp fuse and get tone, so I’m thinking that can’t be it. If the fuse is blown I should not get tone from a continuity test. I also do a voltage test but this was my mistake. I checked the voltage going through the fuse by putting the negative probe on the metal clamp holding one side of the fuse, and the positive probe on the metal clamp holding the other side of the fuse and I see 12.6 volts. The proper way to do this test is to put your negative probe on the negative terminal of a battery and the positive probe on on the metal clamp holding the fuse after current passes through the fuse and heads into the house. Had I done that, I would have seen there is no current flowing past the fuse. But, I don’t know that at this point and I’m thinking the fuse is fine.
So now, I’m definately thinking its the inverter or the transfer switch. Those are the only two things that make any sense. I’d also tested the battery voltage while I was in that bay and I was getting 6.4 volts off of each battery, so those puppies are fully charged and my magnum panel is either lying to me or more likely, I dont know how to interpret what it’s saying to me.
Give Newmar a call, they’re stumped. Start talking to
@Neal who is also talking to
@redbaron and we’re running tests on the inverter, resetting it and everything. Nothing is changing. It’s late, the batteries are fully charged, we’ve got hot water, we’re in southern FL so nothing will freeze overnight and Newmar will be sending a tech the next day. We can survive the night so I call it quits. While all of this was going on, my wife had finished up our dinner at the neighbor’s (I thanked the gentleman and gave him a bottle of Titos as a token of appreciation since we was fond of vodka).
The next morning, I have to run an errand and I’ve heard so much about these 300amp fuses blowing that I decide to grab one at an O’Reilly’s Autoparts store just to keep on hand in case that happens. When I get back that afternoon, I decide to just try and replace it. Maybe I tested something wrong or my multimeter is smoking something. I pop in the new fuse and everything roars back to life. It was the fuse the whole time.
So a couple of lessons here.
1. Read the manual and do what it says in its entirety. Not just the last sentence. Had I done that, I would have solved it the night before (though I didn’t have another 300amp fuse on hand to correct it).
2. Pay attention to your systems. That wasn’t my problem here but it could have easily been. It was entirely possible initially that I’d lost power at the pedestal earlier in the week and didn’t know and my batteries had been discharging the entire time.
3. Learn how to use your multimeter. It’s an invaluable tool. I used it for almost every single test I performed but unfortunately, it was my first time ever using one so I didn’t know exactly what I was doing. Only had a vague idea.
4. Always post on RVForums.com and try to be as accurate as possible. I gave inaccurate descriptions and test results and several folks on here still knew what it was. The amount of knowledge here is amazing.
5. Carry extra 300amp fuses.
6. Always ask what happened two seconds before this incident.
Thanks to everyone who participated in helping me solve it. I hope this post helps someone else down the road.