We had upgraded to a 3000W Hybrid Magnum Inverter in the last RV. The Magnum Hybrid Inverter (MSH) does have Load Support.
The lesser Magnum models do not appear to have Load Support.

Here is the User manual Language regarding Load Support

3.2.3 Load Support While in the Standby Mode and the charger is enabled, the MSH3012RV inverter/charger has the ability to work in parallel with the incoming AC source (utility or generator power) to power the AC loads using current from the batteries. During the Standby mode, the current and voltage from the AC source and the current used by the AC load are continually monitored. When loads on the inverter output exceed the maximum available current from incoming AC source, the Load Support feature is automatically activated. The Load Support feature causes the MSH3012RV inverter/charger to reduce/stop the battery charging operation and begin using current from the batteries along with the maximum available current from the AC source to ensure the AC loads are powered. The Load Support feature turns off once the load demand decreases and there is suffi cient current from the incoming AC source; when this happens, the battery charger is again activated and begins charging the batteries. For the Load Support feature to automatically function, the following needs to occur: 1. An AC source (utility power/AC generator) must be connected. 2. The inverter must be enabled (INV LED is on). 3. The battery voltage must be ≥0.5 volts above the LBCO setting (10 VDC default). Info: If using a remote that is able to show the load support status and the unit is in load support, the status will indicate either “Load Support AAC” or “Load Support VDC”. Info: The load support feature of the MSH3012RV can provide 60 amps on its AC output. For example, if the input AC source is 40 amps, load support can add up to 20 amps; if the input is 50 amps, load support can add up to 10 amps of additional current. Info: The load support feature is monitored thru the AC HOT 1 IN terminal. When the AC HOT 1 IN is the only input connected to the incoming AC source, then load support is provided to the loads connected to both the AC HOT 1 OUT and AC HOT 2 OUT terminals However, if the AC source is connected to both the AC HOT 1 IN and the AC HOT 2 IN terminals [from either a split-phase (120/240VAC) or three-phase (120/208VAC) source], the Load Support feature is only provided and supports the loads connected to the HOT 1 OUT output. In this instance, the AC HOT 2 OUT output is only pass-thru power coming from the AC HOT 2 IN terminal Info: The input amps (or shore amps) setting on the remote control should be set ≥5 AAC for the load support feature to limit and support the incoming amperage correctly. There are two modes of operation within Load Support. • Load Support AAC – In this mode, the AC loads connected to the inverter output are requiring more power than the incoming AC source can provide on its own. The inverter pulls the additional current—that is needed for the loads—from the inverter batteries to keep the incoming AC current from exceeding the input amps setting on the remote control. Info: In Load Support AAC, even though the LED indicators may indicate charging, the inverter/charger may not be putting current into the battery. If using a remote, the Inverter/Charger Amps AC meter indicates the load support process by displaying negative current fl owing from the batteries to the loads. The input amps AC value will also drop during this process, while the load amps AC value remains the same. • Load Support VDC – In this mode, an external DC source (i.e., alternator, solar, etc.,) is causing the battery bank voltage to rise above the temperature-compensated battery voltage setting on the remote control. If this happens, the inverter/charger will reduce the incoming AC current and use current from the batteries to support the inverter load. Info: The charger must be enabled (not in ‘Charger Standby’) and in the Absorb or Float charge mode (with at least a 6-amp inverter load) for the Load Support VDC feature to be active. Note: Load Support VDC is not active in either the Bulk or EQ charge modes.
 
While I'm not smart on that my only thought of is the power coming into the ATS switch. If it's not within params it can shutoff and I think the goal is getting good power, i.e. brown out conditions handled, before the ATS to prevent a disconnect and subsequent AGS start for those with that available and configured.
I’m not either and I don't think it was available when our coaches were built, but since its available now, I would check on a new coach before buying an autoformer.
 
@Joe Goodxrvn after FPU you should take your coach over to Solar Energy Systems in Nappanee and let them give you a little electrical makeover :)

 
I checked the Inverter that is installed in the DCDP on the spec sheet. It is a 2800W inverter. The spec sheet did not specify brand. However, the 2800w Pure Sine Magnum does not offer Load Support. I will check once the DSDP is built to see which inverter brand Newmar installed.
 
If its 2800 its Magnum. They put Victron 3kw inverters in a few of them in 2022 but that might have just been a supply chain thing,
 
If its 2800 its Magnum. They put Victron 3kw inverters in a few of them in 2022 but that might have just been a supply chain thing,
It was supply chain. I got the Victron in my 2022 DSDP from the factory.
 
A reason to make the Autoformer installation modular. The Electrical code in 2020 now allows campgrounds to ban the use of Autoformers. Granted if the Autoformer is installed inside the RV no one would be the wiser, However, I like to follow the rules and respect the campground wishes so I can easily disconnect (unplug) the Autoformer should it be necessary.

Discussion of the Code restrictions:

 
There is clearly some confusion here because the NEC and NFPA are saying that these devices draw more amperage to make up for low voltage, balancing the equation. And the only time the NFPA gets involved is when there is risk of fire - over-heated electrical in this case. But I guess I should say perceived or theoretical risk, because the NFPA does go a bit over the top.

But Hughes says: “The Autoformer DOES NOT take power from the park. It does not affect the park or input voltage, or make electricity. What it is doing is changing the voltage – amperage relationship lowering the amperage [tapping point] and raising the voltage.” By doing this it is also lowering the total available wattage. Something to keep in mind - you can‘t run as much stuff, but at least what you run will be at the proper voltage

The only way it can do this without drawing additional amperage from the pedestal is by lowering the available amperage to the coach (Hughes’ claim), robbing amps to pay volts. This makes sense (again balancing the equation) to protect what you are running from low voltage, but it also reduces your 50amp service, depending on the adjustment, on the coach side of the autoformer. I’d say this is ok, since, if the need exists, you are in a low power situation anyway. Better to regulate it on your side of the pedestal.

Like Mike Sokol, I’d be interested to find out which is true. The test would be simple to perform, but would also be expensive because you’d have to buy an auto-former. So this question will have to be answered by a disinterested third party in possession of an autoformer, and with the curiosity and wherewithal (power supply) to perform the test.

My guess is that Hughes is correct in this case, and the NEC and NFPA are addressing all auto-transformers generically without regard to the specifics of the Hughes device. Otherwise they would have to test all auto-transformers and then specify which ones meet the code and which ones don’t.
 
Last edited:
Thinking about the Autoformer “stealing“ power from the Park. Hughes says that this is impossible. The Park has allocated 30 or 50 amps, depending upon your rig, to your spot. Draw more than the circuit is designed to provide and the circuit breaker will cut power. Looking at it this way, they appear to be correct.
 
UL approved is a requirement to meet code! What that means is the device has been tested, no need to be retested, unless modified.
So the issue that the NEC has is the protection of the grid infrastructure. Transformers are measured in VA (volt amps) close to watts, but there are calculation differences.

Let's take an example and examine it shall we?

We know that as battery voltage drops amp draw increases in order to supply the same watts. If using an inverter to supply the appliance, as the battery voltage drops the inverter demands higher amperage from the battery to supply the designed output voltage. Most quality inverter data confirms this.
When the demand is high enough and the battery voltage is low enough the inverter protects the battery by disconnecting. This protection is not available on the grid, that is why Brown outs occur.
It really is about grid Transformer sizing. When fixed location boost Transformers are installed, they were installed to overcome voltage drops, but the supply Transformer was installed with the anticipated VA ratings, portable boost transformers don't take into account grid equipment, nor protect it in any way.

The reason grids have brown outs is the system has been over taxed. I agree with NEC on this.
 
Thinking about the Autoformer “stealing“ power from the Park. Hughes says that this is impossible. The Park has allocated 30 or 50 amps, depending upon your rig, to your spot. Draw more than the circuit is designed to provide and the circuit breaker will cut power. Looking at it this way, they appear to be correct.
Not true! One needs to understand how service power is calculated, it is a percentage of full loading. Look into the NEC for guidance.
 
The question is whether the Hughes unit draws more amperage from the grid side to maintain 120v to the coach, or reduces available amperage on the coach side to bring voltage up to balance the “volts x amps = watts” equation, lowering available watts to the coach in the process.

Again, from Hughes: “The Autoformer DOES NOT take power from the park. It does not affect the park or input voltage, or make electricity. What it is doing is changing the voltage – amperage relationship lowering the amperage and raising the voltage.”

The NEC/NFPA ruling seems to paint all auto-transformers with the same brush, assuming that they all raise voltage by raising amperage maintaining maximum load capacity. But Hughes is saying the Autoformer steps-down amperage on the coach side of the pedestal to step up voltage thus lowering the maximum load capacity - the opposite of the concern for parks owners and grid operators.

The test I mentioned earlier would confirm which is true. If it is as Hughes says, then there would be no impact on the park side of the pedestal. If Hughes is misrepresenting their product, then yes there would be a problem. But from a regulatory standpoint, I can see how it would be easiest to just say they all violate the electrical code.
 
Last edited:
10% of 120 =12v=108vac 50amp× 108=5400w 50ampsx120= 6000w so it is assumed the primary wire size is limited to 5400w. And although this may be the case it will have an overheating problem if you demand 6000w from it, long before it limits the current. Transformers are designed for a set volt amps. And though that is what they are designed to handle does not mean they can't be abused.
The real issue comes when many units are installed and cause problems with the grid side Transformers.

Not to be a naysayers, the better solution is the system designed to supplement the grid in your rig using the inverter and batteries.
That is elegant!!!

If you want isolation from spikes and isolation transformer is the best,.
 
10% of 120 =12v=108vac 50amp× 108=5400w 50ampsx120= 6000w so it is assumed the primary wire size is limited to 5400w. And although this may be the case it will have an overheating problem if you demand 6000w from it, long before it limits the current. Transformers are designed for a set volt amps. And though that is what they are designed to handle does not mean they can't be abused.
The real issue comes when many units are installed and cause problems with the grid side Transformers.

Not to be a naysayers, the better solution is the system designed to supplement the grid in your rig using the inverter and batteries.
That is elegant!!!

If you want isolation from spikes and isolation transformer is the best,.
I definitely agree that this is not the most elegant solution and I’m saving my pennies for a new ( bigger) inverter that will include load support and a better battery bank to back it up (but not just for this reason). And I have a decent size solar set-up by RV standards. I also think the autoformer is way over-priced for what it is, although not necessarily for what it does. It may be cheap insurance.

As far as abusing the autoformer goes, I guess if you insisted on trying to pull a full load with it in amperage-reduction-voltage-maintenance mode something would have to give, but I would assume that there is thermal protection built in. In fact I believe I read somewhere that it will shut down in the above scenerio.
 
Last edited:
I definitely agree that this is not the most elegant solution and I’m saving my pennies for a new ( bigger) inverter that will include load support and a better battery bank to back it up (but not just for this reason). And I have a decent size solar set-up by RV standards. I also think the autoformer is way over-priced for what it is, although not necessarily for what it does. It may be cheap insurance.

As far as abusing the autoformer goes, I guess if you insisted on trying to pull a full load with it in amperage-reduction-voltage-maintenance mode something would have to give, but I would assume that there is thermal protection built in. In fact I believe I read somewhere that it will shut down in the above scenerio.
Most of thermal shut down schemes can produce sizable spikes. So that can be troublesome, would have to know what they use if that is the case. I would say a zero crossing circuit would have to be used to avoid any problems, I'm wondering if they would disclose!
 