Scissor lift? In my dreams!!! Getting the panels up on the roof was the biggest hurdl.

The 6AWG works great. Early adopters were heck bent on parallel wiring of a bunch of 12v 100w panels. If I am not mistaken...AMSolar and Marvin Braun (PrecisionRV.com) were fans...and added thick cables from the roof to the basement. They have each diversifield since.

Yes...the 6AWG has it’s limitations, and as you point out...setting the panels in a series-parallel configuration will keep you within the amperage limits. I do not know the exact cutoff point..but at some voltage you go into “high voltage” category. In the solar industry...high voltage requires additional safety labels and manual shutoff switches...so I didn’t want to go there either.

Here’s a link that shows different configurations and formulas for calculating the theoretical voltage and amperage for choosing wires and fuses...


In a perfect world/perfect day...1,000 watts per meter sq. sun intensity...I would yield 1,440 watts (8 x 180watt panels). The math worked out nicely...if your batteries absorb setting is around 14.4v...1,440watts will give you 100A of current. My Interstate batteries recommend just a bit below that... ( C/10, or 92.8A). I wired my panels in four strings of two... So, each pair are wired in series...and each string of two are combined in parallel. It’s a balance. MPPT controllers love voltage...they wake up much faster with two panels in series...and can start working. The controller will have a recommended minimum voltage for best power point tracking. I advised another friend...he went with the Magnum PT-100 controller. I used the then current guidance in the Magnum Manual. They later found out the minimum voltage for their controller is higher than they originally thought. The controller works...but throws out an error code...which basically says the voltage is too low to compute maximum power point. I would recommend three panels in series for that controller based on the latest guidance...vs. two in series. During a high output point...I see somewhere around 1,200 watts...and the PV voltage is around 42v...and around 28A going down the 6AWG solar prep wire. The same gauge used in your cord reel to carry up to 50A. I believe the insulation they used on this solar prep wire is rated much higher than 50A...can’t remember what the amperage was that I found..but needless to say it is leaps and bounds more than 28A.

The way we use our coach...we have the minimum I would recommend. The atmosphere doesn’t always give you a full count of wattage. Having a residential refrigerator, microwave, espresso machine....we LIKE power. Seems a few of the high end installs lately have been closer to 2000watts and parallel charge controllers. Might fit on a 45’ coach nicely 😇...

I do like not worrying about power outages, or being able to boondock and not running the Generator a huge amount. I also never worry about coming out to dead batteries. I‘m sure you are already onboard as to the advantages.

The 6AWG is great for what I have. If you were designing a system for 2,000 watts and parallel controllers...then two sets of 6AWG would have been my choice for solar prep.

The BMV-712 that you purchased can pair with certain SmartSolar charge controllers. They use proprietary VE.Smart (BLE) communication. With an optional temperature sensor designed for the BMV-712...the sampled voltage and temperature are relayed to the SmartSolar charge controller. If using Lead Acid chemistry...this is most beneficial as it give you more precise compensation of charge parameters based on battery temperature. LiFePO4...I gather uses no such temperature compensation...but can use the temperature in other ways....such as cutting off solar charge if the batteries get too cold.

I am a big fan of Victron solar products...
 
Last edited:
Joined
Jul 29, 2020
Messages
270
The 6AWG is great for what I have. If you were designing a system for 2,000 watts and parallel controllers...then two sets of 6AWG would have been my choice for solar prep.
There is only to small a wire. The larger the better. If your wire is much above ambient temp you would better have been served with larger wire. Heat is lost power. use your IR thermometer. I have 4 wires coming from the roof, two for each controller in the rig. My MPP is 55 volts.

High voltage according to the NEC2017 is 100+ volts. under that is low voltage. The call of NEC2017 is for an E-shutoff switch that emergency responders have access to. In the past 48 volts was the limit at that voltage NEC had a say if the state adopted it. There is still the "preexisting work " for older systems.
 
Joined
Nov 3, 2019
Messages
143
RV Year
2016
RV Make
Newmar
RV Model
Ventana 4037
RV Length
40’
TOW/TOAD
Jeep JKU
There is only to small a wire. The larger the better. If your wire is much above ambient temp you would better have been served with larger wire. Heat is lost power. use your IR thermometer. I have 4 wires coming from the roof, two for each controller in the rig. My MPP is 55 volts.

High voltage according to the NEC2017 is 100+ volts. under that is low voltage. The call of NEC2017 is for an E-shutoff switch that emergency responders have access to. In the past 48 volts was the limit at that voltage NEC had a say if the state adopted it. There is still the "preexisting work " for older systems.
Thank you for those details. I couldn’t remember what the voltage and safety cutoff requirements were/are...and haven’t stayed abreast of the latest.
 
Joined
Jul 24, 2020
Messages
35
Location
Southern Maryland
RV Year
2018
RV Make
Newmar
RV Model
Mountain Aire
RV Length
45
TOW/TOAD
2015 Jeep GC Overland
So I’ve been trying to figure out some of the basic specs for the panels and the controller.

While I need to procure and install the panels and controller, there are several components that I already have. Those being the AGM batteries, Xantrex SW3012 inverter, AND the 6 AWG solar prep wires from the roof to the basement compartment.

Here are some thoughts. I’m looking for feedback to see if I’m think about this correctly.

My thought is that I want to develop a plan on how I would max out the solar capability. Whether I implement it now or incrementally over time.

It would seem that one of the implementation limitations will be the 6 AWG wire. Looking online, I find that a 6 AWG wire is limited to 55 amps (various based on temperature). If I were to install 12V panels in parallel, the output would be limited to roughly 660 watts (55A * 12V). Obviously I would want more capability than this. If the 12V panels were installed in a series of two and then each series in parallel, the 6 AWG wires could support approximately 1320 watts. That’s much better and in line with numbers that I’ve read in various posts.

I suppose I could combine the panels in a series of four to yield 48 volts and the 6 AWG wire could support unto 2640 watts. That sounds really nice! Am I understanding this correctly?

Also, it seems like panels are available in various voltages to include 12V, 24V, and 48V. If the input to the controller is going to be 48V, would it best to installed 4 12V panels in series, 2 24V panels in series, or just 48V panels. My understanding is that these would be options.

I also have a questions on selecting a MPPT controller, but I’ll post that latter as this post is probably long enough.
 
Joined
Nov 3, 2019
Messages
143
RV Year
2016
RV Make
Newmar
RV Model
Ventana 4037
RV Length
40’
TOW/TOAD
Jeep JKU
You need to use the data plate numbers from your desired panels. They will have Isc (Short Circuit Current)...and Voc (Voltage Open Circuit)...a 12v panel isn't putting out 12v... It appears you were estimating wattage based on 55A x 12V...doesn't work that way. I believe I linked a source pdf which details the computations...and application of safety factors...
 